Shower Drain Odor



To add a comment visit the Article Page.

Comments

Dennard
19 Dec 2007, 15:16
Help please. I live on the 2nd floor of a 3 story 36 unit condo. One of my shower drains emits a foul odor. Scrubbing the shower, pouring vinegar down the drain as well as chlorox provides temporary relief. Once the shower is used again or the 2nd time, the odor returns. Any remedies? Thank you.
AsktheBuilder
19 Dec 2007, 15:22
Dennard,
Did you do all I said to do in this column?
Brian
26 Dec 2007, 13:07
I have the same situation with my shower drain - bad sewer smell. My wife is more sensitive to it, but I can smell the odor if I get close to the actual drain. We followed your suggestions, and we just had the vent system pressurized and no leaks were observed. Did I mention that the house is only 3 years old? Any suggestions on what to do next? So far I haven't found any plumbing service that has the meter to detect the gas and its levels. I am not ready to tear apart my house to chase ghosts. Thanks
AsktheBuilder
26 Dec 2007, 13:16
Brian,
You didn't say if you removed all of the biofilm.
Brian
31 Dec 2007, 12:50
Yes, The biofilm was removed from the drain. There was a small amount of film from soap, but not enough to be a problem. The pressure test passed, and we had 5 days without smell, then one day with smell. Today - no smell. Cannot figure that out. Is the smoke test more effective at detecting leaks, or is the pressure test good enough? The area that is common is the master bath, shower, and toilet. No smell in either two, but same vent.
AsktheBuilder
31 Dec 2007, 13:10
Brian,
If you passed a regulation pressure test, a smoke test is no different. The smoke test just tells you where the leak is. You have no leak.

Are the fixtures squeaky clean?
Brian
02 Jan 2008, 05:24
All fixtures are good and clean - wife is a neat freak. To elaborate on the pressure test, the plumbing contractors sealed the system at 4 locations (roof and cleanouts) and added water to the toilets and sinks creating "pressure". The water levels in the toilets did not move. Is this the same as pressurizing the sewer drain system? Otherwise, I have no other ideas that might be causing the odor. The smell is centralized in the actual drain, but with my wife's sense of smell, she notices it in the room.
AsktheBuilder
02 Jan 2008, 07:05
Brian,
They did the test correctly. This means the source is *surface* bacteria. You need to locate the surface.......
Brian
07 Jan 2008, 05:34
Surface bacteria? The smell still comes and goes. Can a backdraft be created with windy days? No trees and the vent is on the windward side - water in toilets and p-traps move on windy days. Also, the master bath is located under and closest to the actual vent on the roof.
AsktheBuilder
07 Jan 2008, 06:17
Brian,
No, it is not a backdraft issue.
Mya
15 Jan 2008, 19:48
Dear Tim, I have seen your video on how to remove oil stains from concrete/driveway. Do you have any suggestions on the removal of power steering fluid from the driveway? Some stains are new but most are old. Would pressure washing be the best way for removal?
AsktheBuilder
16 Jan 2008, 14:43
Mya,
Power-steering fluid is just another oil. You can try a pressure washer, but be careful!
Jill
03 Feb 2008, 21:55
I live on the 27th floor of a 31 story building. The building was built around 1968. I just remodeled my shower and now have a sewer smell coming from my drain. I have had the super in my building look at it from the floor below. He states there is no leak in the trap. I haven't used the bath in a few weeks due to the renovation but I have filled the trap daily. After 24 hours the smell is back. Can there be a blockage that is causing the trap not to fill properly and leak out? Any other suggestions besides the cleaning that you recommend?
Jeremy
02 Apr 2008, 21:57
My problem sounds a lot like Dennard's above. I have a new house (only 3 months old) and have had an odor coming from a shower since we moved in. It is a tile shower (tile floor and walls). I have water proofed the grout, cleaned the shower with bleach, used drano for any cloggs, and cleaned inside the drain with a long brush down into the trap. We have not used the shower in 2 days and the smell came back even with no use. It does not smell like sulfer so not sure if its sewer gas or not. What can it be?
AsktheBuilder
05 Apr 2008, 17:54
Jeremey,
It sounds like a disconnected vent pipe.
Jeremy
09 Apr 2008, 06:59
The source of the problem was actually the water itself smelling. A disconnected vent would probably mean water would be leaking out on the ceiling down stairs (which it wasn't) so I had my builder go into another one of his houses that was still for sale in the same neighborhood. Turns out it had the same odor. I installed a new shower head with a filter and now the smell is gone with clean water now sitting in the trap.
margaret molitor
05 Jun 2008, 20:57
To clean the bio film, what is the best kind of soap to use to clean it. I am having this problem in my bathroom sink.
Robert
06 Jun 2008, 14:15
I have the same problem. Mine is due to biofilm. However, I clean my pipes and its good for about a week. If I use commercial strenght cleaner, the smell is gone about two weeks. But the film and smell return in just a week or so. Is there anything on the market that can stop the growth of the biofilm. I have this problem in all three bathrooms, tubs and sinks. It is annoying having to clean all my pipes every two weeks, and expensive for the eight bottles of chemicals I use. Any suggestions? I thought about replumbing my house, expensive, but will the problem just come back. I have hard water. I thought about putting a softener on it. Would that help? The reason I thought about that, is that I am the second owner of the house, it is 13 years old. The previous owner had soft water and didn't have that problem. The problem didn't surface until we were in it about a year. When we bought it we hooked up to public water, from well water, which was high in sulfur but very soft, it measured a 2 when we had it tested. Now our public water measures a 6. Since the previous owners did not have any problems like this in the first 8 years, will going back to soft water help to retard or eliminate the biofilm growth? Should I replumb my house and then install a softener? Thanks.
Bob
26 Sep 2008, 21:55
dwon stairs shower is used only once or twice a year.
we run how water down the drain but the smell returns shortlyany suggestions???
Peter
06 Nov 2008, 17:47
Hi Tim,
I am a maintenance tech dealing with a Biofilm issue. One floor of my building has it's A.C. condensate lines (aka indirect wast [IW]) piped down to the janatorial closet on the floor below, where it drops into a slop sink. The sink has a 3" drain line with an old cast iron trap. I was getting the smell backing up into the units above, so I trapped the IW line at the discharge. This cut the smell down on the upper floor considerably. However, the lower floor started to smell, so I set to work cleaning out biofilm from the drain.

I got it! the sink smelled 99% better. Then water trickled out of the IW line... It Stank!! later today, I will be trapping the AC units themselves, and tracking down where this water is coming from (as it is heating season, and the ACs are off). But, I will still have the problem in the closet, due to the fact that the IW line itself is full of biofilm. Short of repiping, what can I do to sweeten that line?
Carmen
08 Nov 2008, 12:58
Hi, I have a similar problem but can't really describe the odor. It smells dusty or maybe musky and it permeates the bathroom. We just bought this home (it's 3 years old) and know that it had a previous leak in the shower that was fixed. Could this be a mold issue as well? The order is constant and is worse when taking a shower. If it's mold then how can this be corrected in the most cost effective manner? Also, the shower shares a mutual wall with our closet and the other wall with the bathtub.
Rick
12 Nov 2008, 18:57
If the trap for the bathtub drain is allowing sewage gas to escape, should we smell it in the tub drain? We have a sewage smell in the bathroom and the plumber seems to think our trap needs to be replaced. But I don't smell anything in the tub drain, even when I put a paper cup with a hole in the bottom over it. And the tub drains fine.
Jim Nyman
16 Nov 2008, 18:27
I have the same problem in a 2nd floor apartment shower. Tenant states that the smell is bad and gets worse as she showers.

Sewer lines have all been cleaned.
Amber
16 Nov 2008, 22:31
Just today, we started to notice a foul odor coming from the drain in our bathtub. I have read several of the articles on your website regarding this issue, but I still have one question. Most of the smells you refer to are sewer smells, sulfur smells, etc. Our smell is a distinct vomit smell. Would that be caused by the same bacteria or another issue?
Susan
24 Nov 2008, 17:25
I have a shower drain in our basement that emits a "urine"-like odor ONLY when the shower has been used. If it is dry, the odor goes away. We have tried many cleaning products, to no avail. Any suggestions? The house is over 35 years old.
Paula Pitts
16 Dec 2008, 11:19
I have noticed an odor from my shower I've flushed the drains; a plumber came in a charged $155.00 to replace the wax ring. The odor comes and goes. I'm replacing the shower door ( the house is 14 years old) Now I'm going to try your method. Do I clean biofilm with bleach, hydrogen peroxide what. Also do I find the drain brush in the local "home depot"? My next step is remove the shower and remodel.
Jerry
25 Dec 2008, 01:23
Short of tearing out the shower and starting over, I believe I have the solution to the foul rotten egg smell coming from a tile or other shower with shower pan liners. The smell is probably not coming from the drain but the space between the floor of the shower and the shower pan liner. The design of the shower drain has openings that are intended to direct water that seeps through the grout or other cracks of the shower into the shower pan liner down the drain. If the mold or bacteria is in this area, simply poring bleach into the drain to settle in the p-trap will not affect the mold or bacteria.

You need to take off the drain cover and plug up your drain about 4 inches below the surface or just past the openings that allow the water to drain from between the floor of the shower and the shower pan liner. Pour bleach into the plugged up drain until you have a good standing of bleach in the bottom of the shower. You may want to even fill it until the whole bottom of the shower is covered with bleach. This should force the bleach into the cavity between the floor of the shower and the shower pan liner. Let it set all day or until the next shower. I could not get a good seal down my drain so it would slowly drain. You may want to add boiling water before you unplug it and let it all drain out. Do make sure that whatever you put down the drain as a stop that you can get it out. I hope this works for you. I did for me. You may have to repeat on a regular (weekly) basis for a while.
Tracy
28 Dec 2008, 22:38
I have read the article. What I noticed is that when it was very cold for several days the urine smell in the shower was gone. As soon as it warmed up again, the odor is again present. We have thoroughly cleaned the drain. Ideas??
Brian
10 Jan 2009, 02:50
Hi. I have an odor problem, but it only occurs when I am using the fireplace. It seems to be coming from the shower.
susan shu
24 Jan 2009, 11:16
I moved into the brand new house but the shower drain is totally stopped, I opened the cover and found the sioux chief mfg company's shower drain has no hole at all, do you think the builder who build the house installed wrong drain?
Melanie
15 Feb 2009, 23:48
We had this problem in our new home in our master bath shower. Since it is just my husband and me, the guest bath on the upper level (same level as master bath) never gets used. The water in the tub trap was evaporating, and we found that if we just run water in the guest tub, the odor in the master shower stopped! Has worked every time the odor returns for 11 years now. Hope your solution is this simple.
Mark
16 Feb 2009, 20:45
Very similar problem. New home. Odor coming from one shower drain. The plumbers have sent cameras through all the vents. Sealed all the drains and filled the lines with water, no water drop. Extended the vents above roof level. Replaced the seal on the toilet in that bathroom. We finally tore out the P trap and replaced it. The odor still came back. The odor came back within 2 weeks of replace the P trap. This has been going on for seven months.
Sharon
01 Apr 2009, 20:18
My house turned one year old a couple days ago. Noticed mold smell coming from one bathroom sink, one year check up, plumber said "Oh, just pour some bleach down the drain every now and then". I've lived in houses all my life - used and new - and this has never been an issue. Bathtub emits mold smell as well - biofilm in the overflow. I can clean what I can see of that...what about what I can't? Also, both bathtub spouts fit badly, come out at an angle, have bad caulking to the tile...I am concerned about getting mold or water damage in the walls or the wall side of the tub or pipes. Is this a valid concern? They've "fixed" both spouts twice now...
Kenny Nguyen
11 Apr 2009, 21:18
have a smell coming out of the drain of my shower when I us it . I have tried a drian care solution , but it still smell like sewer in the shower . If I do not use the shower and go to another shower in my home the smell does not come back for a day . But if I use the shower again and a again then it comes by .....why is that , can you help me get rid of this smell ......
Robert Ball
23 Apr 2009, 13:48
I'm interested in "summer-izing" drains in an Arizona condo. My wife and I spend March and April in Tucson. The building is 40 years old, and occasionally pipes leak in units while snowbirds are gone, causing major damage. We've left our plumbing under pressure, telling a neighbor and a pest service to flush toilets and run water when they check on our condo. This year, I'd like to shut off water and put some slow-evaporating fluid in toilet, tub and sink traps. Is RV antifreeze good for that purpose? Is some other fluid better? It's for more than preventing sewer gas; cockroaches inhabit the sewers beyond our traps.
Marie decker
27 Apr 2009, 07:47
I'd like to hear if they found a solution as I am experiencing the same problem in only one shower drain.
john
05 May 2009, 22:30
I have this same sewer gas smell from my drain,too. In my case, though, it comes from a first floor shower that is not used often, and we just all of a sudden notice a horible odor. It does seem to help to run the hot water for about 10 minutes a couple times a week, but this is getting costly. Any other suggestions?
Kathy
12 May 2009, 09:12
My bathtub/shower drain has a screen you can easily remove by removing the screw. However, there is a heavier brass part underneath that which divides the entry to the drain into 3 parts and I cannot get a bottle brush into it so I can remove the biofilm. It seems to be either moulded into the tub (it's an American Standard Americast tub) or bonded with something that does not release. How do I remove the biofilm in that case?
Tom
12 Jun 2009, 14:02
I experience similar problem as others I guess. When I use bleach/water or a liguid gel foam the issue will stay away for a few weeks - maybe a month at the most, but then it comes back. I guess my question is, what is going on that is causing this to happen in the first place? The home is 3 years old (we are original owners, built new). We never experienced this issue in previous home, same bathing habits and products). So my frustration is why does it keep coming back? Am I not getting it cleaned 100%? Thanks for any further input.
Ryan
30 Jun 2009, 21:38
I'm having similar issues with odor, though it's eminating from multiple drains in my house.
I only recently plumbed the house (new construction) in March 2009 and started using it in the middle of May. I've been noticing the smell (a strong sewer smell, particularly strong after showers) since the middle of June.
There are no water backups, meaning all water is flushing/draining everytime I run the shower, sinks, or toilets. Thoughts? Could it be some biofilm/sewage problem below all the fixture drainage points?
Help please!
Ryan
robin
08 Jul 2009, 17:21
Maybe this will help... I live in a 3 story townhouse and I would smell a sewer odor in the master bath (on the 3rd floor) every once and a while. But I could not figure out where or why. I called my plumber and he told me to pour water down the floor drain that is under my washer and dryer. Apparently, this is a drain that never gets used and therefore any water that had been in the pipes had evaporated. Allowing sewage to come back up the pipe. So, once you pour water down the drain, the sewage cant come back up.

It worked! I have not smelled the odor in over a week!
Erich Jackson
20 Oct 2009, 19:07
We had this problem for months, and tried every recommendation on this page as well as others. When I was showing it to my dad, I happened to take off the drain cap and the plastic strainer that we used, and ask him to see if he smelled anything from the drain. He couldn't detect anything, and neither could I. Then our sudden insight came: the plastic strainer and the drain cap smelled terribly - which was the very thing we removed everytime we tried something, and the thing we put back every time. Once I replaced both of those - and cleaned the screw holes - the odor was gone.
Robert
28 Oct 2009, 11:29
We tried everything mentioned here and elsewhere, to no avail. Sewer odor most common while showering, bleach would clear it up for a day or so, trap was functioning well, drain was clean and draining fine. Our shower is cultured marble (acrylic), professionally installed about 12 years ago when the house was new.
SOLUTION: Stagnating water was collecting between the acrylic shower floor and the shower pan liner (membrane). We discovered this when we demo'd the shower for a remodel. If you have an acrylic shower or other non-tile shower, consider standing water in between the shower floor and the liner as a possible culprit. Fixing it would not be easy, though, unless you are tearing out the old shower as we did.
kalia
02 Nov 2009, 00:02
Hi, Did any of you solve this problem? I have a TERRIBLE sewer gas smell and I have tried everything in this column and then some! I've replaced the p-trap, added a second one, snaked and camered all the lines and all the vents, installed new vents, had smoke tests done, had 4 plumbers look at the problem, cleaned the drains and all the pipes with cleaners and brushes, used bleach, draino, pipe cleaner, pro biotics, replaced my main lateral line, filled the vents with water to detect blockages, opened up all the walls to look for leaks or broken vents -- NOTHING has found the problem! Please help!
The smell comes ONLY after or while running the shower. If I cover the drain and run the water, there is no smell. It's MUCH worse if I uncover the drain and let a large amount of water drain at once. It goes away a little bit if I don't use the shower for a month, but then comes back full force after using it once. Any ideas?
Don
06 Nov 2009, 14:44
I had success with Kaboom foaming toilet bowl cleaner. I put a dose on a sheet of paper and rolled the paper into a tube that would fit into the overflow tube. After dumping the tube of Kaboom powder into the overflow tube I added about 6 oz of water. Then, as the foam filled the bathtub drain, I blocked the drain to force the foam up the overflow tube. I let the foam subside by itself. After a week the musty smell has not returned. (I'm hoping that not thoroughly flushing the drain and overflow pipe will retain a film of cleaner that will retard the biofilm.)
James
22 Nov 2009, 11:22
Sani-Drain makes a product that suspends from the drain cover and it is full of enzymes and microbes that eat away on the bio-film that collects as well as eliminates odors.

It is comes in scented or unscented.
I know this product works very well.

I think the website is sani-drain.com
Howard
26 Nov 2009, 20:02
We recently moved into a 12 year old home in Florida. We had an odor coming from our shower after use. My wife is a cleaning fanatic - and she tried most of the items you suggested. My wife suggested it was a problem with our water supply, but since it was only in the shower, I was skeptical.

During a renovation of the bath, I removed the old cultrued mable walls, and shower pan. There was standing water under the pan.

Now with a new concrete and tile floor, with the water gone, the odor is gone.


IBK
12 Dec 2009, 16:53
Brian,

Don't know if you're still actively responding to this thread, but I have a shower drain odor situation too. Mine is unique, actually. I've tried using vinegar, bleach, a combination of the two (yes, I was careful with proportions ... I'm aware of the dangers), Drano ... nothing has helped up to this point.

Now here's where my case gets interesting. Every time I simply run water down the drain, no matter how long it takes, there is never any odor. Hot or cold, doesn't matter. At some point I suspected that the foul odor I was getting was somewhat similar to the soap I was using: Irish Spring Body Wash "Moisture Blast". I hypothesized that the strong odor immediately after showers was directly connected to the soap, so I tried using a different soap. Voila - no odor after the shower!

Keep in mind that I've been using this same soap for many months, and this issue just suddenly started recently. So there's definitely something in that drain that's reacting with my soap to produce that vile odor. Do you have an idea what it might be and the best way to get rid of it?

I have no idea if this is related or not, but I am currently also dealing with an ant infestation around the area. So far I'm trying to use Terra borax baits; their numbers have reduced but they're still there and it's been a few days.
Mags
17 Jan 2010, 19:13
My sister had the same problem with the shower downstairs. The plumber did not put a p-trap in the drain coming out of the shower drain to the main drainage system.

(from wisegeek.com): Codes require a p-trap (or an s-trap) any place there is an open drain line that flows into the drain-waste-vent system. As the name implies, the drain-waste-vent system removes solid, liquid or gas waste from the home through drains and vents. For example, as the water empties from a sink, it goes through the p-trap, on to the drain line, and ends up in the sewage system.

The important thing about the p-trap is that it is has a water seal along the curve of the trap. The seal prevents noxious air or gases to backflow from the sewer line, but the original waste can still exit into the sewage system. If the gases were allowed back into the home, not only would they smell, but they could cause illnesses and have even been known to explode. )

It's amazing but some of these contracting plumbers with a contractors license are more stupid than a smart moron. You need to have a professional plumber check your drainage system to see if you have a p-trap. This is a lifetime investment and worth your peace of mind.
James
21 Jan 2010, 13:42
Hello there,
I am new to this site but need your assistance.

I recently had a new shower in my basement. To do this it was necessary to saw through the cement floor and run new plumbing from the shower to the main downdrain (?) that connected all of the upstairs drains from 2 1/2 baths.
Since this installation there is a foul odor coming from the drain in the new shower.
We do not have this odor in the other showers upstairs and all of the plumbing is new from the new shower to the main drain.
Besides the new shower there is a new sink and toilet all connected to the same new plumbing.
What might be the source of this odor and how might we eliminate it?
The house is 30 years old and this is the first time we have experienced this problem.

Thank you
Jim
Wendi
21 Feb 2010, 15:02
Tim,

Thank you so much for having this solution on your website. I had resolved that perhaps I would have to get a plumber to investigate the odor coming from my master bathroom sink & shower. No need! We did exactly what you suggested and it's like a brand new bathroom.

Thank you!
Mark Schreiber
11 Mar 2010, 14:16
I have heard of the problems with Sewer gases and for some it’s because of a dried out P-trap or something of that sort. Most comments seem to be more focused on the smell arising after the bathroom was just used. One solution that I found to stop sewer gases from entering the house via floor drain is a product called The SureSeal. Take a look and let me know if it fixes your problem :) website is www.thesureseal.com
toni comstock
30 Mar 2010, 13:52
Tim,
I have read your possible causes for the foul smell coming from my shower drain. But this is coming from both the drains in two different bathrooms. What are the chances it is mold?
toni
Michele Atkins
04 Apr 2010, 10:01
When my neighbor upstairs takes a shower water comes into my bath tube along with the smell you all are referring to?

I also called a plumber who snaked out the pipes and found nothing?

Aside from you previous suggestions, what could the water coming up along with the smell mean?

It happens intermittently.

Thanks so much
chris williams
06 Apr 2010, 20:05
Whenever, someone takes a shower I can smell a foul odor in the bathroom. After about a couple of hours it is usually gone. What is this and is there anything I can do to correct this problem. I have tried everything.
Kalia
06 Apr 2010, 22:46
Hi,
I worked for over 9 months trying to eliminate the odor from my shower drain. We added a second p-trap, camered the lines, replaced pretty much all the drain lines and the sewer lateral... tried all the cleaning suggestions. All to no avail. I had to demo my shower (and it was expensive travertine!) It turns out that the shower pan was installed correctly and there was standing water under the tile (even though I hadn't used that shower in months). I was also quite sick every time I used that shower. We took it down to the studs, rebuilt the pan with the help of a shower forensic specialist, and it's been 5 months since then and no smell and no illnesses!
james
08 Apr 2010, 09:51
Shower has sewer odor in newly installed shower.
New mud bed, backer board, framing, vinyl membrane, drain, pipes, p-trap.
No leaks. I filled the p-trap with fresh water..still have sewer odor. Tile is next.
Kelly
01 Jun 2010, 11:33
I have the same exact problem as Brian in a brand new house. Order comes and goes. Squeaky clean. No leaks.
Mike
13 Jun 2010, 19:50
My problem, attempted solutions, and results, sound exactly like Brian. Cleaning the drain down to the trap squeaky clean, temporarily stops the odor for around a week. Thereafter, bleach poured down the drain offers a temporary fix that may last 3 to 5 days, then the stench returns. We have lived in our home since it was brand new 18 years ago and never experienced this problem until several months ago. My wife is gonna drive me nuts if this thing doesn't get fixed.
Susan
07 Jul 2010, 07:48
We have a horrible odor that seems to be coming out of the shower head. The water smells like rotten eggs mixed with hair dye or something awful! After the shower is on for even seconds, my whole bedroom smells like sulfur. It makes me ill. What could it be?
Joel
10 Aug 2010, 15:56
Brian, drain odor comes from my bathtub drain AND from my new washing machine. I suspect that the washing machine and bathtub share the same 'P-trap' somewhere behind the wall and the washing machine is actually the source of the odor. (The user guide for the washer mentions recommends running the 'Clean Washer' cycle to eliminate any odor problem - works for a day or two.) Any suggestions? Thanks
Shelly
31 Aug 2010, 00:14
Hi Tim! I so appreciate all of your blogs and the information that you share and your guidance! For the past 2 years we have been dealing with this shower odor problem (only when water is running down it). Our house is 6years old. We were told different things by different professionals. However, this is the 1st time I have ever heard of Biofilm! Read in depth all your suggetions. We snaked the drain to ensure there were no clogs. The buildup was rock hard on inside of the pipes. I used my steam cleaner with the long attacthments to loosen it up. Which it did- quite a bit. I then used a foaming soap with water and scrubbed the long vertical pipe. I was amazed @ how clean it looked afterward! When I ran the water I still smelled it BUT it was VERY faint. I let the water run for about a good 30mins, the odor practically disappeared! I believe it will probably just take a few showers before the smell will be completely gone. In the meantime I am going to get the Foaming Draino to help "scrub" the pipes a bit more. Thank you sooo much! You are the 1st person who has made any sense in regards to this "mess"! God Bless and THANK YOU again!
~Shelly~
Patty
29 Sep 2010, 07:33
We have a sewer smell but only when the tub is drained. I don't smell anything at all when it's only the shower draining.
Maxs
05 Oct 2010, 00:09
My husband and I live in a one story home for about 4 years now and have the odor that is metioned in the previous comments in the master bedroom shower drain.At first we thought it was the toilet because the wax seal had deteriorated,plummer did that job.Smell is not as bad but still there so I went to the stall removed the strainer and noticed air coming up out of the pipe.I took my flash light and checked for the goo and such,see a small amount. As I look further down it seems that the pipe coming from the shower is not covering the pipe thats carrying the water down.Looks like the pipe is half covering one another is this normal? Poured water down the hole and the air puffed up the smell.Have'nt tried the 50/50 yet or the brush part but I'm willing to try.I do see standing water.
Will in Utah
15 Nov 2010, 22:16
PROBLEM SOLVED. For me anyway, and hopefully this will help someone else. I tried following the advice found here and in other forums and other sites. Nothing worked. Finally I noticed that there were small cracks in the caulking around the drain itself. I removed all the caulking and unscrewed the drain from the drain base in the floor. What I found was rather disgusting and is best described as biosludge. Most showers should have some sort of a shower pan liner. It is there to protect against leaks if your drain should fail, or the shower floor should leak in some other way. In my case the water was leaking into the liner (which feeds into the drain under the shower floor) and the "biofilm" built up over time. I cleaned out the sludge, screwed the drain back in, resealed it with silicon and no more odor. Hope that helps.
Patty
20 Nov 2010, 22:26
Hmmm maybe know what's up with mine. One day while draining the bathwater I noticed I could hear the water that was draining in my sink. I then realized the smell was actually coming from the sink not the tub. I put some RV digester in and it cured it for several weeks. Still not sure what is causing it but at least I can get rid of it for awhile. My house is a 1936 cottage with a very old system.
Pete Owens
03 Dec 2010, 10:20
Was this ever resolved? Just wondering if the venting is adequate. If not the flushing of the master andpossibly other toilets may be sucking some water out of the master shower trap each time a toilet is flushed. If the shower is not used again before the water level in the trap becomes low enough to allow fumes to pass into the shower you get the smell again. I would check the vent sizing and the possibility of a bird or insect nest in the vent pipe(s).
Also, construction debris in the sewer lines for the toilet(s) may be another possibility causing the toilet water to backwash into the shower trap at times when flushed.
jesse
28 Dec 2010, 17:23
We are having very similiar problems with our upstairs shower. We have gone thru all the checks. One contractor suggested that we soak the drain area overnight with "simple green pro 3" cleaner that would penetrate the area that might have bacteria buildup. We have not tried this yet, but it makes sense. We have tried everything else. Does anyone have results of anything like this?
Kim
23 Mar 2011, 23:45
I have a mold smell coming from the bathroom, I'm just not sure from where. We've been in the house 7 months with no problems. It's my daughter's bathroom, but she never uses the shower in there...she likes ours. Her toilet developed a leak in the last few weeks, from the tank, that has yet to be fixed. However...it is not leaking. We just turned the water off until my husband can fix it. So now, the bathroom is not being used at all. The water did leak through to the ceiling of the bathroom below us...staining the ceiling in that room. I pulled the trim around the cabinets and there's no mold there. I can't identify exactly where the smell is coming from other than definately the bathroom. Suggestions on where to go with this?
Thanks!
Tizza
01 Sep 2011, 12:08
Our master shower has a prefab plastic "tub" The drain is higher than the edges and always has water in it. Is there an easy way to cut the drain down to lower the center of the shower floor so that it will drain properly?


To add a comment visit the Article Page.

Contact us to Advertise on this site.